  • Black Obsidian - Tuesday, April 28, 2015 - link

    I've always hoped for more in-depth coverage of the OpenCompute initiative, and this article is absolutely fantastic. It's great to see a company like Facebook innovating and contributing to the standard just as much as (if not more than) the traditional hardware OEMs.
  • ats - Tuesday, April 28, 2015 - link

    You missed the best part of the MS OCS v2 in your description: support for up to 8 M.2 x4 PCIe 3.0 drives!
  • nmm - Tuesday, April 28, 2015 - link

    I have always wondered why they bother with a bunch of little PSU's within each system or rack to convert AC power to DC. Wouldn't it make more sense to just provide DC power to the entire room/facility, then use less expensive hardware with no inverter to convert it to the needed voltages near each device? This type of configuration would get along better with battery backups as well, allowing systems to run much longer on battery by avoiding the double conversion between the battery and server.
  • extide - Tuesday, April 28, 2015 - link

    The problem with doing a datacenter wide power distribution is that at only 12v, to power hundreds of servers you would need to provide thousands of amps, and it is essentially impossible to do that efficiently. Basicaly the way FB is doing it, is the way to go -- you keep the 12v current to reasonable levels and only have to pass that high current a reasonable distance. Remember 6KW at 12v is already 500A !! And thats just for HALF of a rack.
  • tspacie - Tuesday, April 28, 2015 - link

    Telcos have done this at -48VDC for a while. I wonder did data center power consumption get too high to support this, or maybe just the big data centers don't have the same continuous up time requirements ?
    Anyway, love the article.
  • Notmyusualid - Wednesday, April 29, 2015 - link

    Indeed.

    In the submarine cable industry (your internet backbone), ALL our equipment is -48v DC. Even down to routers / switches (which are fitted with DC power modules, rather than your normal 100 - 250v AC units one expects to see).

    Only the management servers run from AC power (not my decision), and the converters that charge the DC plant.

    But 'extide' has a valid point - the lower voltage and higher currents require huge cabling. Once a electrical contractor dropped a piece of metal conduit from high over the copper 'bus bars' in the DC plant. Need I describe the fireworks that resulted?
  • toyotabedzrock - Wednesday, April 29, 2015 - link

    48 v allows 4 times the power at a given amperage.
    12vdc doesn't like to travel far and at the needed amperage would require too much expensive copper.

    I think a pair of square wave pulsed DC at higher voltage could allow them to just use a transformer and some capacitors for the power supply shelf. The pulses would have to be directly opposing each other.
  • Jaybus - Tuesday, April 28, 2015 - link

    That depends. The low voltage DC requires a high current, and so correspondingly high line loss. Line loss is proportional to the square of the current, so the 5V "rail" will have more than 4x the line loss of the 12V "rail", and the 3.3V rail will be high current and so high line loss. It is probably NOT more efficient than a modern PS. But what it does do is move the heat generating conversion process outside of the chassis, and more importantly, frees up considerable space inside the chassis.
  • Menno vl - Wednesday, April 29, 2015 - link

    There is already a lot of things going on in this direction. See http://www.emergealliance.org/
    and especially their 380V DC white paper.
    Going DC all the way, but at a higher voltage to keep the demand for cables reasonable. Switching 48VDC to 12VDC or whatever you need requires very similar technology as switching 380VDC to 12VDC. Of-course the safety hazards are different and it is similar when compared to mixing AC and DC which is a LOT of trouble.
  • Casper42 - Monday, May 4, 2015 - link

    Indeed, HP already makes 277VAC and 380VDC Power Supplies for both the Blades and Rackmounts.

    277VAC is apparently what you get when you split 480vAC 3phase into individual phases..
  • Kevin G - Tuesday, April 28, 2015 - link

    Excellent article.

    The efficiency gains are apparent even using suboptimal PSU for benchmarking. (Though there are repeated concurrency values in the benchmarking tables. Is this intentional?)

    I'm looking forward to seeing a more compute node hardware based around Xeon-D, ARM and potentially even POWER8 if we're lucky. Options are never a bad thing.

    Kind of odd to see the Knox mass storage units, I would have thought that OCP storage would have gone the BackBlaze route with vertically mount disks for easier hot swap, density and cooling. All they'd need to develop would have been a proprietary backplane to handle the Kinetic disks from Seagate. Basic switching logic could also be put on the backplane so the only external networking would be high speed uplinks (40 Gbit QSFP+?).

    Speaking of the Kinetic disks, how is redundancy handled with a network facing drive? Does it get replicated by the host generating the data to multiple network disks for a virtual RAID1 redundancy? Is there an aggregator that handles data replication, scrubbing, drive restoration and distribution, sort of like a poor man's SAN controller? Also do the Kinetic drives have two Ethernet interfaces to emulate multi-pathing in the event of a switch failure (quick Googling didn't give me an answer either way)?

    The cold storage racks using Blu-ray discs in cartridges doesn't surprise me for archiving. The issue I'm puzzled with is the process how data gets moved to them. I've been under the impression that there was never enough write throughput to make migration meaningful. For a hypothetical example, by the time 20 TB of data has been written to the discs, over 20 TB has been generated that'd be added to the write queue. Essentially big data was too big to archive to disc or tape. Parallelism here would solve the throughput problem but that get expensive and takes more space in the data center that could be used for hot storage and compute.

    Do the Knox storage and Wedge networking hardware use the same PDU connectivity as the compute units?

    Are the 600 mm wide racks compatible use US Telecom rack width equipment (23" wide)? A few large OEMs offer equipment in that form factor and it'd be nice for a smaller company to mix and match hardware with OCP to suit their needs.
  • nils_ - Wednesday, April 29, 2015 - link

    You can use something like Ceph or HDFS for data redundancy which is kind of like RAID over network.
  • davegraham - Tuesday, April 28, 2015 - link

    Also, Juniper Networks has an ONIE-compliant OCP switch called the OCX1100 which is the only Tier1 switch manufacturer (e.g. Cisco, Arista, Brocade) to provide such a device.
  • floobit - Tuesday, April 28, 2015 - link

    This is very nice work. One of the best articles I've seen here all year. I think this points at the future state of server computing, but I really wonder if the more traditional datacenter model (VMware on beefy blades with a proprietary FC-connected SAN) can be integrated with this massively-distributed webapp model. Load-balancing and failovering is presumably done in the app layer, removing the need for hypervisors. As pretty as Oracle's recent marketing materials are, I'm pretty sure they don't have an HR app that can be load-balanced on the app layer in alongside an expense app and an ERP app. Maybe in another 10 years. Then again, I have started to see business suites where they host the whole thing for you, and this could be a model for their underlying infrastructure.
  • ggathagan - Tuesday, April 28, 2015 - link

    In the original article on these servers, it was stated that the PSU's were run on 277v, as opposed to 208v.
    277v involves three phase power wiring, which is common in commercial buildings, but usually restricted to HVAC-related equipment and lighting.
    That article stated that Facebook saved "about 3-4% of energy use, a result of lower power losses in the transmission lines."
    If the OpenRack carries that design over, companies will have to add the cost of bringing power 277v to the rack in order to realize that gain in efficiency.
  • sor - Wednesday, April 29, 2015 - link

    208 is 3 phase as well, generally 3x120v phases, with 208 tapping between phases or 120 available to neutral. Its very common for DC equipment. 277 to the rack IS less common, but you seemed to get hung up on the 3 phase part.
  • Casper42 - Monday, May 4, 2015 - link

    3 phase restricted to HVAC?
    Thats ridiculous, I see 3 Phase in DataCenters all the time.
    And Server vendors are now selling 277vAC PSUs for exactly this reason that FB mentions. Instead of converting the 480v main to 220 or 208, you just take a 277 feed right off the 3 phase and use it.
  • clehene - Tuesday, April 28, 2015 - link

    You mention a reported $2 Billion in savings, but the article you refer to states $1.2 Billion.
  • FlushedBubblyJock - Tuesday, April 28, 2015 - link

    One is the truth and the other is "NON Generally Accepted Accounting Procedures" aka it's lying equivalent.
  • wannes - Wednesday, April 29, 2015 - link

    Link corrected. Thanks!
  • SuperVeloce - Wednesday, April 29, 2015 - link

    From Mass storage: "Compared to hard disks optical media touts greater reliability, with Blu-ray discs having a life expectancy of 50 years and some discs could even be able to live on for a century."

    Yeah sure. Like my expensive gold color cd's from different vendors, baked on different high quality writers, now mostly not working anymore after some 15-20 years. Despite being held in almost perfect environment all these years
  • Uplink10 - Wednesday, April 29, 2015 - link

    Someday they are going to figure out that:
    -SAS HDDs are costlier but if you are using RAID it does not matter, they should use consumer drives and not overpriced enterprise drives
    -I calculated sometimes back if Bluray cold storage is cheaper than HDDs but it is not and more so you cannot change the data once you write it, it is better to go with HDDs
  • toyotabedzrock - Wednesday, April 29, 2015 - link

    You have to wonder what these networking chip vendors are hiding in the firmware that makes them so resistant to open sourcing the code.
  • Casper42 - Monday, May 4, 2015 - link

    Johan, some of the HP info at the end was interesting, but incomplete.
    If you (or anyone reading this) plan to talk to HP, they will also talk about their relatively new CloudLine "CL" type machines as well.
    They come in standard 1RU/2RU designs as well as OpenRack designs coming soon.
    And the SL line is all being morphed over to Project Apollo which uses the XL prefix.
    Apollo 2500 is now live, 4X00 will replace SL4500, 6000 has already replaced S6500, and the 8000 was a net-new add for Gen9 focused on big HPC farms.
    So anything SL is, or soon will be, a dead platform. (The SLs you mention could be an exception since they are not widely commercially available)
  • Netpower - Tuesday, June 2, 2015 - link

    One general problem with this design is how to take care of power line disturbances entering the power shelves via the 277V AC lines. The 48V DC is filtered via the 48V battery but you must add a filter/power line conditioner somewhere to make sure that transients and sags doesn't kill your power shelves. The 380V DC approach by (http://www.emergealliance.org) is much more reliable and still have all the advantages with higher efficiency, lower cable losses etc.
  • Astana - Wednesday, September 16, 2020 - link

    It is believed that the nicotine addiction of a smoker prevents you from quitting. But modern research has shown that the quitting process is complicated by psychological addiction. That's why many people can't cope with the habit of smoking. But there are results with https://heroindetoxeurope.com/ drvorobjev hospital they're all successful.
    The problem of smoking is not only the problem of men, but also increasingly - women. Many women are wondering: "How can you quit smoking and not get better? Psychologists have proven that when a woman quits smoking, she subconsciously tries to replace, to compensate for the process of smoking with food. This feeling is also familiar to men who quit smoking, but they do not attach much importance to it. As a result, very soon an extra 3-4 kg or more will appear.